Have been asked to perhaps pin a electrical guide on "Electrical supplies/installations" for a Marquee disco/band etc
I'll try and cover everything from what I know, and what i've experienced as a sparky.
The information following is a General guide, and the individual should contact the NICEIC or ECA for futher information if the occasion should arise where he/she is unsure what to do or a potential dangerous installation is noted?
We all gig at time to time in a marquee. If you are gigging in a marquee in the future you should be asking the questions below to the person booking the disco (client) or in the second place, the marquee operator/installer (competent person who installed the power facility)
The responsibility of the incoming power for the marquee lies with the person who installed the supply!!
The power supply should be installed and tested to electrical safety ""BS7671 electrical regulations""
The power supply installed into the marquee should be done by a qualified person or a competent person who is able to verify and certify that the tempory installation is safe and comlpies with BS7671 and the electricity at work act
please read the following guidence off the internet on marquee supplies.....
ELECTRICITY INSTALLATIONS IN MARQUEE'S
All temporary low voltage systems (415V or less) on the site will be subject to the “Electricity at Work Regulations 1989” .
All electrical installations should be carried out by a competent electrician familiar with the requirements of the above legislation and should operate to the standards recommended by the Institute of Electrical Engineers. Anyone who provides electrical apparatus for their own or anyone else’s demonstration etc. Should before it is connected to the electrical supply, arrange for its testing by a competent electrician and documentation should show the date of the test and the name of the person carrying out the test. All equipment should be connected to the supply through a residual current device (RCD) and all cables and connections where not protected by a weather proof structure shall be of such construction or as necessary protected to prevent, so far as is reasonably practicable, danger arising from such exposure. Socket outlets should not be over loaded, extension leads should not be used indiscriminately. All mains connected portable and transportable electrical equipment should be installed and used in accordance with HSE Guidance note PM32 “safe use of portable electrical apparatus”. All temporary installations must be safely disconnected and removed from the site after the event. .
more info can be obtained from this web site
http://www.iee.org/Publish/WireRegs/Wiring...nt_purposes.pdf
Questions to ask if the supply is already available when you turn up......
what is the voltage and what is the power current/load available to you?
Is the electrical supply run off mains supply or generator supply
Has the electrical supply been installed and certified as stated above
You do not need to get involved in running power into the marquee. This should be done already for you.
Its not the DJ's Job to rig up power to the marquee. If you do this, your putting yourself at risk from prosecution if something goes wrong, or somebody gets hurt from your actions.
Stick to what you do best...DJ! IF You cannot certify the power supply and therefore should not be doing it!
ok, so you turn up and there is no electricty to the marquee!
What can you do
Run a couple of extention leads from the house to the tent? I suppose you've got no choice really. But try to get the customer to do this for you if you can? (takeds the onus off you) This isnt really deemed as "Marquee electrical installation" its more deemed as a "portable power lead" so BS7671 does not apply in this case. But the electrical leads should still be installed with safety in mind.
As a minimum the extention leads should be PVC or rubber sheathed. Should be able to carry 500v, should be PAT tested regulary and inspected regulary.
The extention lead supplies into the marquee "MUST" be attached at source to an RCD (Residual Current Device)
RCD devce should be 30 milliamp tripping
This means that if the RCD unit "sees" more than 30milliamps of leakage from live or neutral conductors.....it will trip! this actually equates to 50v (meaning that if an RCD is used, no more than 50v can flow to earth or ground before tripping the circuit)
50v has been designed as human "touch voltage" hence why RCD's are set at 30milliamps for this purpose.
Anyway moving on.....general common sense should prevail. The lead cant be installed so it "hangs someone" when they walk past. reasonable steps should be taken to install the leads with safety in mind, tripping hazards etc. This part is down to you.....if your leads from 13amp socket outlets are strung around the marquee, someone gets hurt.....get your public liability docs out!!
so in a nutshell, tempory feeds into a narquee thats bigger than 13amp (taken off a distribution board and not plugged in) should be done by a competent person who can certify the work before use
Extention leads should be safely insalled powered from 13amp socket outlets at the hose, but through RCD device at source...(not at the cd player end!!)
all extention reels shold be fully unwound to counteract the coil effect (cable creating eddie currents and heating up)
All extention cables should be large enough to cope with your demand and fuse correctly at the source plug.
ie a 13amp lead should be 1.5mm flex and fused at 13amps
1.0 cable extention may be fused at 10amps at the plug
Generator supplies
Do not get involved in the installation of a genny. Let the marquee people or sparky do this. You just want a couple of 13amp supplies at the end of the cable!
As long as your stuff is ok, tested (PAT) and you use RCD's.....and install your stuff out of reach etc....then your ok!
Genny voltage must be 230v +/- 10volts max. Your equipment should be ok with this fluctuation.
Again, check with the installer of the machine and look at the certificate (your right to do this before plugging in)
supply frequincy 50 hz no question/no butts!
anything else please ask away
cheers Jeff
regards Jeff